What it is
One failed sensor can take down an entire 1-Wire network, and finding the fault often means opening walls.
This project is a transparent inline hub that splits one 1-Wire bus into eight independent branches while continuously measuring each branch.
To the controller it still looks like a standard 1-Wire network. Existing sensors keep their original ROM IDs, and no firmware changes are required.
What it measures
Fault location. An open cable becomes "Branch 3, ~34 m" instead of "Sensor missing."
Cable length, to about ±15%.
Degradation over time. Repeatability is around 1%. The device records a baseline at commissioning and watches for drift. An 8% rise over two weeks means moisture in a junction box — visible months before the first CRC error.
The right pull-up. It measures the branch and picks 4.7k, 1k, or active. Normally you find this by trial and error.
Real fault types. Short, open, and dead sensor are three different states, not one "no response."
Signal margin. How wide the valid read window is, in µs. The narrower it gets, the closer the line is to failing.
How the measurement works
Pull the line to ground, release it through a known resistor, and time the rise with a comparator. That gives you the line's capacitance, and capacitance gives you length.
C = t / (R · ln 2) at a 50% threshold.
50% rather than the textbook 63.2%: a divider made from two identical resistors has the lowest relative error, and supply drift cancels because the divider and the reference share a rail.
On RP2350 this runs in PIO — two instructions per count at 150 MHz, about 4 pF of resolution.
Absolute accuracy isn't the goal. Repeatability is.
Why star topology breaks
Capacitance. 50 m of twisted pair is roughly 2.75 nF. Through a 4.7k pull-up that's τ ≈ 14 µs, against a 1-Wire time slot that allows 10–15 µs to recover. The line never gets back up in time.
Star makes it worse, because every branch's capacitance sits in parallel on one driver, permanently.
Parasite power is worse than most people realize
In parasite mode a DS18B20 adds roughly 800 pF to the line, against about 25 pF when externally powered.
One parasite-powered sensor is capacitively equivalent to 14 m of cable. Eight of them contribute more capacitance than 50 m of the cable itself.
Which is the point of the whole project — the thing that breaks the bus is a number you can measure.
Hardware
Limits
Open questions
Status
Design phase. Analog front end and measurement method worked out, PCB not routed yet. Firmware plan: USB and configuration first, slave emulation second, so the riskiest part isn't being debugged at the same time as new hardware.