This Blog is about making a nutrient dosing system for hydroponics that is plug and play, I didnt quite get it to the full stage of plug and play with this version. But it is almost there. Because the change of nutrient strength of our systems can be modelled as a linear system with respect to nutrient delivery it should be possible to implement a very simple self tuning control system based on the system model. Why a Self Learning system:
>System only needs to be roughly defined
>Adapt for pump wear
>Adapt for a change in nutrient source strength
>Plug and Play for a wide variate of Systems
>No problem dealing with the Lag between delivery and stable reading
I made this control system with Urine as a nutrient source and because the concentration of urine can vary we need a system that can take this into account. A traditional PID controller will struggle here [Or at least I would struggle to implement a good one] because of the large lag between input and output measurement due to the mixing of nutrients in the system [Tank mixing+Grow beds fill+drain time]. It will also work for traditional liquid fertalizer.
Main Variables in the script
>Tank size in L
>Nutient Strength [Stick with 100 or follow hints in the code]
>Pump Size [L.Second-1]
Variables input by LCD Screen:
>EC Set point
>Probe Calibration
The only real choices hardware wise:
Pump sizing
Although this is a self learning system we still need to choose a nutrient pump of a suitable size so the pumping interval is quite large to reduce the effect of pump priming and post pumping discharge [Fancy words for the pump acts weirdly when we first turn it on and just after we turn it off].
I have not included the maths here to fine tune your pump size because it doesnt matter that much, just pick a pump with a flow rate of less than 10% of your main tank volume per minute.
EC Probe
Using the Cheap DIY Probe: Pick a plug as a probe that isnt used in your country [currently supports EU and USA two prong]
[This will also work with a comercial ec probe, just change the getec() to your Ec meter]
Pinout:
Code:
ElCheapo Arduino EC-PPM measurments and Nutrient Doser Script
This scrip uses a common USA two prong plug and a 1Kohm Resistor to measure the EC/PPM of a Aquaponics/Hydroponics Sytem.
Then It Increases the Nutrient content until the set point is reached
It Also Estimates the EC of the nutrient Source [For when you are using Urine/ unknown Nutrient EC]
28/8/2015 Michael Ratcliffe Mike@MichaelRatcliffe.com
This program is free software: you can redistribute it and/or modify
it under the terms of the GNU General Public License as published by
the Free Software Foundation, either version 3 of the License, or
(at your option) any later version.
This program is distributed in the hope that it will be useful,
but WITHOUT ANY WARRANTY; without even the implied warranty of
MERCHANTABILITY or FITNESS FOR A PARTICULAR PURPOSE. See the
GNU General Public License for more details.
You should have received a copy of the GNU General Public License
along with this program. If not, see .
Parts:
-Arduino - Uno/Mega
-Standard American two prong plug
-1 kohm resistor
-DS18B20 Waterproof Temperature Sensor
-FluidPump [Smaller is better];
Limitations:
-Cell Constant [K] and ECSetpoint must be less than 5.0 or it will Mess with the way we save values in EEPROM
-A reset will change your set point and kell constant slightly, but not to a great extent
-EEPROM seems to survive a reflash, so changing values in the code will not change them in the flashed software. you will need to do it via the LCD
See www.MichaelRatcliffe.com/Projects for a Pinout and user guide or consult the Zip you got this code from
//************************** Libraries Needed To Compile The Script [See Read me In Download] ***************//
// Both below Library are custom ones [ SEE READ ME In Downloaded Zip If You Dont Know how To install] Use them or add a pull up resistor to the temp probe
#include
#include
#include //Standard LCD Lbrary
#include //Standard EEPROM Library
//************************* User Defined Variables ******************************************************//
// Rememebr to ad .0 after any float definition or it will return to an initiger, ie 1.0 not 1
//********************** System Information *************************************//
float TankSize =10; //SystemVolume in Liters
float PumpRate=0.; //Flow rate of dosing pump in L per min
long DosingInterval =60; //How often you want to dose the tank in minutes, hour intervals will be fine for most systems
long MixingTime =30; //The time for mixing of nutrients in minutes [I have a lot of water flow so 60 seonds is fine for me, if in doubt increase it to half a hour]
int Pump =14; //Pin Controlling relay for nutrient Pump
int OFF =0;
int ON=1;
//****************************** System EC Value *******************************//
//Changes for what plants you are growing, sun intensity and temperature
//###If you are using urine in a system and have not yet got a established Bacteria bed set this to ECSetpoint=0.7 for a week to let the bacteria become established##
float ECSetpoint =1.0; // How Strong you want the water system to be nutrient wise
//******************** Nut Tank EC *********************************************//
//the code will optimise this number after every dosing, so we are selecting the highest end and allowing the arduino to work the rest out its self
//You are using a nutrient that states the NPK and not a overpriced one that used the words "Boost" "flower" "Super" but hides the important NPK ratios?
//If not Save yourself a fortune and switch to a cheap one that is honest about its NPK
//We need to put in a estimated start point for the controller to start with
//For an estimate take the EC Estimate= (N*20) + (P*8.8) +(K*16)
float ECFluidEstimate =100.0; //if you dont know the value stick with 1000, it will sort itself out
//***********************************EC Meter **********************************//
//----------- Do not Replace R1 with a resistor lower than 300 ohms ------------
int R1= 1000; //The resitor we placed in voltage divider
int Ra=25; //Resistance of Arduino Digital Pins
//float Rp=0; //Resistance of figure 8 connector
int ECPin= A8;
int ECGround=A9;
int ECPower =A12;
//************ Temp Probe Related *********************************************//
#define ONE_WIRE_BUS 26 // Data wire For Temp Probe is plugged into pin 10 on the Arduino
const int TempProbePossitive =22; //Temp Probe power connected to pin 9
const int TempProbeNegative=24; //Temp Probe Negative connected to pin 8
float MinT=100;
float MaxT=0;
float Temperature=0.0;
//************************* User Defined Variables ********************************************************//
float CalibrationEC=1.380; //EC value of Calibration solution is s/cm
//*********** Converting to ppm [Learn to use EC it is much better**************//
// Hana [USA] PPMconverion: 0.5
// Eutech [EU] PPMconversion: 0.64
//Tranchen [Australia] PPMconversion: 0.7
// Why didnt anyone standardise this?
float PPMconversion=0.5;
//********************** Cell Constant For Ec Measurements *********************//
//Mine was around 2.9 , with plugs being a standard size they should all be the same
//I Recommend Calibrating your probe but if that is not an option at this time the following cell constants [K] will give a good estimated readout:
//EU plug: K= 1.76
//US Plug K= 2.88
float K=2.88;
//*************Compensating for temperature ************************************//
//The value below will change depending on what chemical solution we are measuring
//0.019 is generaly considered the standard for plant nutrients [google "Temperature compensation EC" for more info
float TemperatureCoef = 0.02; //this changes depending on what chemical we are measuring
//***************************** END Of Recomended User Inputs *****************************************************************//
// select the pins used on the LCD panel
LiquidCrystal lcd(8, 9, 4, 5, 6, 7);
// define some values used by the panel and buttons
int lcd_key = 0;
int adc_key_in = 0;
int button =0;
#define btnRIGHT 1
#define btnUP 2
#define btnDOWN 3
#define btnLEFT 4
#define btnSELECT 5
#define btnNONE 6
int Screen =1;
//Max number of screens on lcd
const int Last_Screen_no =6;
//used to debounce input button
int buttonLast=0;
OneWire oneWire(ONE_WIRE_BUS);// Setup a oneWire instance to communicate with any OneWire devices
DallasTemperature sensors(&oneWire);// Pass our oneWire reference to Dallas Temperature.
float EC=0;
float EC25 =0;
int ppm =0;
float raw= 0;
float Vin= 5;
float Vdrop= 0;
float Rc= 0;
float PumpTime=0; //Variable for pumping duration
long MixingInterval=0; //variable for when to check new EC
float PostDocingEC=0;
float PreDosingEC =0;
long StartDosingMillis =0;
int NutesAdded=0;
long time=0;
//********************** Some Variables For Loging Min/Max Values ********************************//
float MinEC=100;
float MaxEC=0;
//************************** Just Some basic Definitions used for the Up Time LOgger ************//
long Day=0;
int Hour =0;
int Minute=0;
int Second=0;
int HighMillis=0;
int Rollover=0;
//**************************Some Stuff For Calibration ******************************************//
float TemperatureFinish=0;
float TemperatureStart=0;
int i=0;
float buffer=0;
float Kt=0;
//***********************Some Stuff for Self Learning and Errors********************************//
float LastGoodEstimate= 0;
float PumECRateStart=0;
float PumECRate=0;
int error=6; // 6 means no error
long Doses=0;
long LastRun=0;
int ECHold=0;
//*********************** EPROM Stuff [So SetPoint and Cal Survive a reboot] ******************//
int value;
int addresSetpoint=10;
int addresCalibration=0;
//*********************************Setup - runs Once and sets pins etc ******************************************************//
void setup()
Serial.begin(9600);
Splash_Screen();
Read_Eprom();
pinMode(TempProbeNegative , OUTPUT ); //seting ground pin as output for tmp probe
digitalWrite(TempProbeNegative , LOW );//Seting it to ground so it can sink current
pinMode(TempProbePossitive , OUTPUT );//ditto but for positive
digitalWrite(TempProbePossitive , HIGH );
pinMode(ECPin,INPUT);
pinMode(ECPower,OUTPUT);//Setting pin for sourcing current
pinMode(ECGround,OUTPUT);//setting pin for sinking current
pinMode(Pump,OUTPUT);//setting pin for sinking current
digitalWrite(Pump,OFF); //makes sure we are starting from a stop
digitalWrite(ECGround,LOW);//We can leave the ground connected permanantly
delay(100);// gives sensor time to settle
sensors.begin();
//****************Converting to milli seconds********************//
DosingInterval =DosingInterval*60000; //Coveerting to milliseconds
MixingTime =MixingTime*60000; // Converting to milliseconds
MixingInterval=DosingInterval+MixingTime;
PumpRate=PumpRate/60.0; //converting to L.Second-1
//***************Converting to MCU related units ****************//
PumECRate=ECFluidEstimate*(PumpRate/TankSize); // EC.Second-1
PumECRate=PumECRate*2.0;//Just incase people overestimated some values
LastGoodEstimate=PumECRate;
PumECRateStart=PumECRate;
R1=(R1+Ra); //Taking into acount Digital Pin Resitance
GetEC(); //gets first reading for LCD and then resets max/min
MinEC=100.0;
MaxEC=0.0;
MinT=100.0;
MaxT=0.0;
//******************************************* End of Setup **********************************************************************//
//************************************* Main Loop - Runs Forever ***************************************************************//
//Moved Heavy Work To subroutines so you can call them from main loop without cluttering the main loop
//Dont Measure the EC more than once every five second "GetEC()" or you will get bad readings and wear your probe out
void loop()
//*********Takes care of millis rolover**************//
if(millis()<=5000){
NutesAdded=0;
delay(5000);
//*********Check if it is time to dose the system, we wont dose it if the probe is broken or if we are colse to the setppoint ********//
if( (button==1 || millis()%DosingInterval<=1000) && (error>=4 && EC25<=(ECSetpoint-0.1) && NutesAdded==0) ){
NutrientAddition();
NutesAdded=1;
Doses++;
//********This fine tunes for the perticular system **************//
if((millis()>=(PumpTime+MixingTime+StartDosingMillis)) && NutesAdded==1){
EstimateEC(); // Goes to the script to estimate the nutrient source EC
NutesAdded=0;
//********** Runs the Function to estimate the EC of the hydroponics system **********//
if (millis()%5000<=1000 && ECHold==0){
GetEC();
ECHold=1;
if (millis()%5000>=1000){
ECHold=0;
//**************** Turns the pump off at the end of the pumping time********************//
if (millis()>=StartDosingMillis+PumpTime){ //Still need to take care of millis rollover!?
read_LCD_buttons();
read_Temp();
Log_Min_MaxTemp();
uptime();
Calibration();
ChangeECSetpoint();
Error();
PrintReadings(); // Cals Print routine [below main loop]
//************* Stopinf Funky Readings From unmixed solution**********//
if(NutesAdded==0) Log_Min_MaxEC();
delay(50);
//************************************** End Of Main Loop **********************************************************************//
//***************************** Function to read temperature ********************************//
void read_Temp(){
sensors.requestTemperatures();// Send the command to get temperatures
Temperature=sensors.getTempCByIndex(0); //Stores Value in Variable
//*******************************Turns on Pump To Dose System *********************************//
void NutrientAddition(){
PreDosingEC =EC25; //Makes note of the initial EC
PumpTime=1000*((ECSetpoint-PreDosingEC)/PumECRate);
StartDosingMillis=millis();
digitalWrite(Pump,ON);
//******************************** System Automatd Learning ************************************//
//This Function optimises the dosing volume for the main tank volume and Strength of Nutrient tank
void EstimateEC(){
PostDocingEC=EC25; //Makes Note of the EC at the end of the addition
//*********Rapidly change EC Estimation on startup************//
if(PostDocingEC>=(PreDosingEC+0.05)){
PumECRate =(1000.0*((PostDocingEC-PreDosingEC)/PumpTime));
else PumECRate=PumECRate/2.0;
//************ This Loop Is called From Main Loop************************//
void GetEC(){
//*********Reading Temperature Of Solution *******************//
raw= analogRead(ECPin);
//************Estimates Resistance of Liquid ****************//
digitalWrite(ECPower,HIGH);
//raw= analogRead(ECPin);
raw= analogRead(ECPin);// This is not a mistake, First reading will be low beause if charged a capacitor
digitalWrite(ECPower,LOW);
//***************** Converts to EC **************************//
Vdrop= (Vin*raw)/1024.0;
Rc=(Vdrop*R1)/(Vin-Vdrop);
Rc=Rc-Ra;
EC = 1000/(Rc*K);
//*************Compensating For Temperaure********************//
EC25 = EC/ (1.0+ TemperatureCoef*(Temperature-25.0));
ppm=(EC25)*(PPMconversion*1000);
//***********This Loop Is called From Else Where- Prints to serial usefull info **************//
void PrintReadings(){
Serial.print("EC: ");
Serial.print(EC25);
Serial.print(" Simens ");
Serial.print(ppm);
Serial.print(" ppm ");
Serial.print(Temperature);
Serial.print(" *C ");
Serial.print("PumpRate EC/s: ");
Serial.println( PumECRate);
//** First Screen Shows Temp and EC **//
if(Screen==1){
lcd.setCursor(0,0);
lcd.print("Arduino EC-PPM ");
lcd.setCursor(0,1);
lcd.print("EC: ");
lcd.setCursor(3,1);
lcd.print(EC25);
lcd.setCursor(9,1);
lcd.print(Temperature);
lcd.print("'C");
//** Second Screen Shows PPM **//
else if(Screen==2){
lcd.setCursor(0,0);
lcd.setCursor(0,1);
lcd.print("PPM: ");
lcd.setCursor(4,1);
lcd.print(ppm);
lcd.setCursor(9,1);
lcd.print("'C");
//**Third Screen Shows Min and Max **//
else if(Screen==3){
lcd.setCursor(0,0);
lcd.print("Min: ");
lcd.setCursor(4,0);
lcd.print(MinEC);
lcd.setCursor(9,0);
lcd.print(MinT);
lcd.print("'C");
lcd.setCursor(0,1);
lcd.print("Max: ");
lcd.setCursor(4,1);
lcd.print(MaxEC);
lcd.setCursor(9,1);
lcd.print(MaxT);
lcd.print("'C");
else if(Screen==4){
lcd.setCursor(0,0);
lcd.print("Uptime Counter: ");
lcd.setCursor(0,1);
lcd.print(" ");//Clearing LCD
lcd.setCursor(0,1);
lcd.print(Day);
lcd.setCursor(3,1);
lcd.print("Day");
lcd.setCursor(8,1);
lcd.print(Hour);
lcd.setCursor(10,1);
lcd.print(":");
lcd.setCursor(11,1);
lcd.print(Minute);
lcd.setCursor(13,1);
lcd.print(":");
lcd.setCursor(14,1);
lcd.print(Second);
else if(Screen==5){
lcd.setCursor(0,0);
lcd.print("Factors ");
lcd.setCursor(8,0);
lcd.print("PPMC:");
lcd.setCursor(13,0);
lcd.print(PPMconversion);
lcd.setCursor(0,1);
lcd.print("K: ");
lcd.setCursor(2,1);
lcd.print(K);
lcd.setCursor(9,1);
lcd.print("a:");
lcd.print(TemperatureCoef);
else if(Screen==6){
lcd.setCursor(0,0);
lcd.print("EC.Sec-1: ");
lcd.setCursor(10,0);
lcd.print(PumECRate,5);
lcd.setCursor(0,1);
lcd.print("Doses: ");
lcd.print(Doses);
else if(Screen==7){
lcd.setCursor(0,0);
lcd.print("EC Setpoint: ");
lcd.setCursor(12,0);
lcd.print(ECSetpoint,3);
lcd.setCursor(0,1);
lcd.print("Hold Select Change ");
if((millis()%6000)<=3000){
//************************* Printing any errors we have ***********//
if (error==1) {lcd.setCursor(0,0);
lcd.print("Error: ");
lcd.setCursor(8,0);
lcd.print(error);
lcd.setCursor(0,1);
lcd.print("Probe Problem "); }
else if (error==2) {lcd.setCursor(0,0);
lcd.setCursor(8,0);
lcd.print(error);
lcd.setCursor(0,1);
lcd.print("Large Overshoot "); }
else if (error==3) {lcd.setCursor(0,0);
lcd.setCursor(8,0);
lcd.print(error);
lcd.setCursor(0,1);
lcd.print("Temp Problem "); }
else if (error==4) {lcd.setCursor(0,0);
lcd.setCursor(8,0);
lcd.print(error);
lcd.setCursor(0,1);
lcd.print("Pump Problem "); }
else if (error==5 ) {lcd.setCursor(0,0);
lcd.setCursor(8,0);
lcd.print(error);
lcd.setCursor(0,1);
lcd.print("System Learning "); }
else;
//********** Usued for Debugging ************
Serial.print("Vdrop: ");
Serial.println(Vdrop);
Serial.print("Rc: ");
Serial.println(Rc);
Serial.print(EC);
Serial.println("Siemens");
//********** end of Debugging Prints *********
//****************************** Reading LCd Buttons ****************************//
void read_LCD_buttons(){
adc_key_in = analogRead(0); // read the value from the sensor
// my buttons when read are centered at these valies: 0, 144, 329, 504, 741
// we add approx 50 to those values and check to see if we are close
if (adc_key_in > 1000) button =0;
else if (adc_key_in < 50) button =1;
else if (adc_key_in < 250) button =2;
else if (adc_key_in < 450) button =3;
else if (adc_key_in < 650) button =4;
else if (adc_key_in < 850) button =5;
//Second bit stops us changing screen multiple times per input
if(button==2&&buttonLast!=button){
Screen++;
else if (button==3&&buttonLast!=button){
Screen--;
if (Screen>=Last_Screen_no) Screen=Last_Screen_no;
if(Screen<=1) Screen=1;
buttonLast=button;
//******************************* LOGS Min/MAX Values*******************************//
void Log_Min_MaxEC(){
//**********So We dont Get First Few Readings**********//
if( Doses==5){
MinEC=100.0;
MaxEC=0.0;
if(EC25>=MaxEC) MaxEC=EC25;
if(EC25<=MinEC) MinEC=EC25;
void Log_Min_MaxTemp(){
if(Temperature>=MaxT) MaxT=Temperature;
if(Temperature<=MinT) MinT=Temperature;
//******************************* Checks if Select button is held down and enters Calibration routine if it is ************************************//
void Calibration(){
if(Screen!=5) return;
if(button!=5) return;
else delay(1000);
read_LCD_buttons();
while(1){
read_LCD_buttons();
lcd.setCursor(0,0);
lcd.print("Set Calibration EC ");
lcd.setCursor(0,1);
lcd.print("EC: ");
lcd.setCursor(3,1);
lcd.print(CalibrationEC);
if (button==2) CalibrationEC=CalibrationEC+0.01 ;
if(button==3) CalibrationEC=CalibrationEC-0.01;
if(button==1) break;
delay(100);
lcd.setCursor(0,0);
lcd.print("Calibrating ");
lcd.setCursor(0,1);
lcd.print("EC: ");
lcd.setCursor(3,1);
i=1;
buffer=0;
TemperatureStart=sensors.getTempCByIndex(0); //Stores Value in Variable
while(i<=10){
buffer=buffer+raw;
i++;
delay(5000);
raw=(buffer/10.0);
TemperatureFinish=sensors.getTempCByIndex(0); //Stores Value in Variable
EC =CalibrationEC*(1+(TemperatureCoef*(TemperatureFinish-25.0))) ;
//***************** Calculates R relating to Calibration fluid **************************//
Vdrop= (((Vin)*(raw))/1024.0);
Rc=Rc-Ra; //Taking into account pin resistance
Kt= 1000/(Rc*EC);
if (TemperatureStart==TemperatureFinish ){
Serial.println(" Results are Trustworthy");
Serial.print("Calibration Fluid EC: ");
Serial.print(CalibrationEC);
Serial.print(" S "); //add units here
Serial.print("Cell Constant K");
Serial.print(K);
lcd.setCursor(0,0);
lcd.print("GoodResults ");
lcd.setCursor(0,1);
lcd.print("EC: ");
lcd.setCursor(3,1);
lcd.setCursor(9,1);
lcd.print("K:");
lcd.print(Kt);
while (1) { // wee need to keep this function running until user opts out with return function
read_LCD_buttons();
if(button==4) return; //exits the loop without saving becauser user asked so
if (button==5){
K=Kt; //saving the new cell constant
//******8*Saving the new value to EEprom**********//
value=K/0.02;
EEPROM.write(addresCalibration, value);
lcd.setCursor(0,0);
lcd.print("Saved Calibration ");
lcd.setCursor(0,1);
lcd.print("K: ");
lcd.setCursor(3,1);
lcd.print(Kt);
delay(2000);
return;
if(millis()%4000>=2000){
lcd.setCursor(0,0);
lcd.setCursor(0,1);
lcd.print("EC: ");
lcd.setCursor(2,1);
lcd.setCursor(9,1);
lcd.print("K:");
lcd.print(Kt);
else{
lcd.setCursor(0,0);
lcd.print("Select To Save ");
lcd.setCursor(0,1);
lcd.print("Down to Exit ");
else{
Serial.println(" Error Wait For Temperature To settle");
while (1) {
read_LCD_buttons();
if(button==2) Calibration();
if(button==3) return;
lcd.setCursor(0,0);
lcd.print("Bad Results ");
lcd.setCursor(0,1);
lcd.print("Press DWN Exit ");
//**************************************** End OF CALIBRATION ROUTINE ******************************//
//**************************************Start OF Function To Change EC Setpoint*********************//
void ChangeECSetpoint(){
if(Screen!=7) return;
else delay(1000);
read_LCD_buttons();
while(1){
read_LCD_buttons();
lcd.setCursor(0,0);
lcd.print("Set EC SetPoint ");
lcd.setCursor(0,1);
lcd.print("R:exit EC: ");
lcd.print(ECSetpoint);
if (button==2) ECSetpoint=ECSetpoint+0.01 ;
if(button==3) ECSetpoint=ECSetpoint-0.01;
if(button==1) {
value=ECSetpoint/0.02;
EEPROM.write(addresSetpoint, value);
break;
delay(100);
//*******************************End OF Change EC Setpoint *********************************************//
//*********************************Function to Check for any errors**************************************//
void Error(){
error=6; //For Some Reason the Errors are not refreshing like they shoud, this fixes it
//*********Checking if the Probe is in the Solution********//
if(EC25<=0.05){
Serial.println("Probe Problem: Check it is in the liquid and not shorted ");
error=1;
//***********Checking if we seriosly overshot the setpoint**//
else if((EC25>=(ECSetpoint*1.3))&& NutesAdded==0){
Serial.println("Dosing Problem: We overshot the setpoint, Will attempt to fix its self ");
error=2;
//******** Checking Temp Probe is In range ****************//
else if((Temperature>=50.0) || (Temperature<=0.5)){
Serial.println("Temperature Problem: Check Wiring [Also Check Probe has pull up] ");
error=3;
//****** Checking Dosing Pump Is working******************//
else if( (PostDocingEC<=(PreDosingEC+0.05) ) && (NutesAdded==0 && EC25<=ECSetpoint-0.2) ){
Serial.println("Dosing Problem: Check Nute Tank is full and pump is not broken ");
if(Doses<=10){
//Still Geting a good estimate for the EC
//error=5;
if(Doses>=11) {
//Proberbly a pump problem
error=4;
else error=6;
//************************** Printing somthing useful to LCd on start up **************************//
void Splash_Screen(){
lcd.begin(16, 2); // start the library
lcd.setCursor(0,0);
delay(1000);
lcd.print("Nutrient Doser");
lcd.setCursor(0,1);
delay(1000);
lcd.print("Mike Ratcliffe");
lcd.setCursor(0,1);
delay(1000);
lcd.setCursor(0,1);
lcd.print("Free Software ");
delay(1000);
lcd.setCursor(0,1);
delay(1000);
lcd.setCursor(0,1);
delay(1000);
lcd.setCursor(0,0);
lcd.print("To Calibrate ");
lcd.setCursor(0,1);
lcd.print("Hold Select ");
delay(3000);
lcd.setCursor(0,0);
lcd.print("To Navigate ");
lcd.setCursor(0,1);
lcd.print("Use Up-Down ");
delay(3000);
//********************************************* Check what values we have stored in eprom ******************************//
void Read_Eprom(){
//************** Restart Protection Stuff ********************//
//Setpoint
value = EEPROM.read(addresSetpoint);
//the 254 bit checks that the adress has something stored to read [we dont want noise do we?]
if (value <=254) ECSetpoint=value*0.02;
//Calibration
value = EEPROM.read(addresCalibration);
if (value <=254) K=value*0.02;
//************************ Uptime Code - Makes a count of the total up time since last start ****************//
void uptime(){
//** Making Note of an expected rollover *****//
if(millis()>=3000000000){
HighMillis=1;
//** Making note of actual rollover **//
if(millis()<=100000&&HighMillis==1){
Rollover++;
HighMillis=0;
long secsUp = millis()/1000;
Second = secsUp%60;
Minute = (secsUp/60)%60;
Hour = (secsUp/(60*60))%24;
Day = (Rollover*50)+(secsUp/(60*60*24)); //First portion takes care of a rollover [around 50 days]
Michael Ratcliffe
Thnx by the way.
https://wp.josh.com/2014/06/23/no-external-pull-up-needed-for-ds18b20-temp-sensor/
All the info can be found here
Please repost your libraries.
Hello, can you email the the modified libraries? I cannot find it at
Yes it did. Thank you for your awesome help!
gonna test it on a small greenhouse and let you know of results!
Hello Micheal,
I got the same problem with this error message:
The sketch name had to be modified. Sketch names can only consist
of ASCII characters and numbers (but cannot start with a number).
They should also be less than 64 characters long.
In function 'void loop()':
'ChangeECSetpoint' was not declared in this scope
ChangeECSetpoint();
'Error' was not declared in this scope
Error();
In function 'void LogEC()':
integer overflow in expression [-Woverflow]
In function 'void Calibration()':
Self_Learning:806: error: expected '}' at end of input
lcd.setCursor(0,0);
Looks like copy and paste didnt do the full code, its updated now and should work :)
Thanks a lot, yeah i used your modified libraries and now it works
Bear in mind this code is only a proof of concept, I would recommed setting some min/max values for the self optimisation EC/second part :)
Hello Micheal,
after i verify the code i get the following error message
any ideas? am i missing anything?
Thanks for your help
see above comment reply :)
Thanks for the reply that worked well.
After uploading the code, i encountered the following:
-EC value and ppm are different from the reading i took using the calibration code (previous one) for the same calibration solution.
- Screen 7 : EC set point does not appear, the code only takes first 6 screens.
- When i switched screen 7 and screen 6 just to view the EC set point, the select button does not do anything so basically i could not do any calibration as well.
On some LCD's the buttons adc ranges are different, can you try:
void read_LCD_buttons(){ adc_key_in = analogRead(0); // read the value from the sensor
else if (adc_key_in < 50) button =1; // Right?
else if (adc_key_in < 195) button =2; //UP?
else if (adc_key_in < 380) button =3; //Down?
else if (adc_key_in < 555) button =4; //Left?
else if (adc_key_in < 790) button =5; // Select
Working?